Topic: 2008 NEC Exam Prep, Wrong Answer?

User: dsereni, Location: San Francisco Bay Area

Asked on: Thursday, February 17, 2011 at 4:42 pm EST
Answered on: Tuesday, May 14, 2024 at 1:44 am EDT

Question: I seem to have found an incorrect answer to a question in Mike Holts Illustrated Guide to NEC Exam Preparation 2008Unit 5, Table 5 question asks: What is the cross sectional area for one 1/0 XHHW Compact Conductor?The Answer given as correct is [c] 0.2733 sq in?Referring to Chpt 9, Table 5A (Compact Copper & Aluminum Wire Nominal Dimensions and Area) I find the answer to be 0.1352.Answer [c] is the cross sectional area of one 4/0 XHHW Compact Conductor.Can someone show me the error of my ways?

It appears that you are correct. The answer given in Mike Holt's Illustrated Guide to NEC Exam Preparation 2008 is incorrect.The cross-sectional area of a 1/0 XHHW compact conductor is indeed 0.1352 sq in, as per Table 5A in Chapter 9 of the NEC. The cross-sectional area of a 4/0 XHHW compact conductor is 0.2733 sq in.

Here is the correction for the question in Unit 5, Table 5

What is the cross-sectional area for one 1/0 XHHW Compact Conductor?(a) 0.0533 sq in(b) 0.1352 sq in

(c) 0.2733 sq in
(d) 0.2980 sq in Flag for review