User: noeernlat, Location: Washington State
Asked on: Thursday, February 17, 2011 at 4:58 pm EST
Answered on: Tuesday, May 14, 2024 at 1:44 am EDT
Question: I need a little help understanding something here. I have a 3 phase 125A panel listed on the plans as being fed by 1 1-2" Conduit containing (4) 1AWG conductors and (1) 6AWG conductor. The calculated load for this panel is 14.8 Kva, if I'm correct this equates to a calculated load of 41 A. Now, I assume i have to derate due to 4 or more current carrying conductors which is 1 AWG (90deg Column) 150 X.80= 120A. Am I permitted to supply this gauge wire to a 125A panel even if the calculated load is 41A?? Im thinking I would need to run 1/0 Conductors. Thanks!
Yes, you can supply 1 AWG conductors to a 125A panel, even if the calculated load is 41A.Explanation
The calculated load of 41A is only a fraction of the ampacity of the 1 AWG conductors. The 125A panel is oversized to provide headroom for future expansion or unexpected loads. The conduit size is adequate for the conductors, even after derating for multiple current-carrying conductors (41A × 3 = 123A < 150A × 0.8 = 120A).
Derating
The ampacity of conductors must be derated when there are more than three current-carrying conductors in a conduit. For 1 AWG conductors in a 90°C column, the derating factor is 0.8. This means that the ampacity of each conductor is reduced from 150A to 120A.
Panel Oversizing
Panels are typically oversized to accommodate future load growth or unexpected peak loads. The 125A panel provides ample margin for the current load of 41A.
Conclusion:
Based on the provided information, supplying 1 AWG conductors to a 125A panel is acceptable and meets applicable electrical codes. Flag for review