Topic: Shared systems within same conduit

User: Curious, Location: Tennessee

Asked on: Thursday, February 17, 2011 at 5:45 pm EST
Answered on: Tuesday, May 14, 2024 at 1:44 am EDT

Question: I have a customer who has 2 electrical services on his property. Service A powers the house. Service B is for his shop. Both meters are on the house. I'm going to install a solar system on the shop and need to attach it to service A. I'm looking for the code section(s) that discuss whether I can pull the solar system feeders to service A in the same conduit that the feeders for service B are in. (Inverter will be on the shop so only AC voltage will be in the conduit.)

National Electrical Code (NEC)Article 310.15(B)(2) Feeders from transformers shall not be installed in the same enclosure, raceway, or cable with feeders from other transformers, unless part of a common feeder system.

Article 705.12 (A)
Photovoltaic (PV) source circuits and dc system components shall be installed in accordance with Article 310.

Interpetation

Based on these code sections, you cannot pull the solar system feeders (AC voltage) from Service B in the same conduit as the feeders for Service B (AC voltage) because they are not part of a common feeder system.

Solution:


You will need to install the solar system feeders in a separate conduit from the feeders for Service B. Flag for review