User: DisconnectingMeans, Location: Utah
Asked on: Thursday, February 17, 2011 at 10:43 pm EST
Answered on: Tuesday, May 14, 2024 at 1:45 am EDT
Question: I recently came across an odd existing installation and I was curious wether or not it was necessarily a code violation. I've been reading through the 2011 handbook and haven't come across a situation that confirms or denies this fact. The original installers ran the pipe runs directly above medium bay light fixtures and attached the conduit to a box connected to the fixture through means of a chase nipple. And the conduit was strapped within the three foot rule through use of mini straps mounted to holes on either side of the fixture. They dropped 1/4 inch all-thread down to support the conduit within the span from the fixture and the trusses if it ever exceeded the ten foot strapping rule and also strapped the run of EMT to each beam for added rigidity... It seems to be a solid installation. Any comments, code references ,thoughts or information anyone might feel they could share would be helpful.
NEC 2011 Code References
Article 300.11 - Raceways shall not be the support for luminaires, fixtures, switches, or other devices. Article 300.12 - Conduit shall be secured to boxes, cabinets, and fittings by proper means. Article 314.23(F) - Attachment to Lights: Junction boxes, fittings, or other enclosures shall not be attached to the mounting means of lighting fixtures. Article 410.16(A) - Luminaires (Fixtures): Luminaires shall be attached to outlets in a manner that will secure them in place and without damage to the conductors, connections, or the luminaire.
Interpretation
Based on the provided description and the cited code references, the installation may be in violation of the NEC for the following reasons:
Conduit Support
The conduit is being attached to the lighting fixture box through a chase nipple, which violates Article 300.11 by using the fixture as support for the conduit.
Junction Box Attachment
The junction box connected to the fixture should not be attached to the fixture's mounting means, as required by Article 314.23(F).
Fixture Attachment
The luminaires do not appear to be securely attached to the outlets, as they are only supported by the conduit drops from the fixture box.
Possible Solutions
To address the code violations, the following solutions could be considered:
Provide Separate Support
Install an independent support system for the conduit, such as strut or unistrut, to properly support it without relying on the fixture.
Use a Fixture Conduit Body
Install a conduit body specifically designed for attaching conduit to lighting fixtures, which meets the requirements of Article 314.23(F).
Secure the Luminaires
Properly attach the luminaires to the outlets using safety cables, suspension brackets, or other approved methods to ensure their secure installation.
Conclusion:
The described installation does not fully comply with the NEC requirements, as it relies on the lighting fixtures for conduit support and junction box attachment, and does not provide adequate securement of the luminaires. To ensure code compliance and maintain a safe installation, the recommended solutions should be implemented. Flag for review