Question: I have never seen this before until today. A residence with a 200 amp underground service to a meter, then two 100 amp SEU cables tied together on the load side lugs going into the house to two separate 100 main breaker load centers right next to each other. Both panels have their neutrals and grounds bonded together. Are there violations here other than the fact that the neutral is connected to ground at two different places? Was this a common practice at one time? Installation is about 50 years old.
Yes, there are several code violations here:1. Multiple Neutral Connections to Ground
The neutral and ground conductors should only be connected at the service panel. Connecting the neutral to ground at two different locations creates a parallel path for current flow, which can lead to overloading and overheating of the neutral conductor or other components.2.
Undersized Service Conductors
For a 200-amp service, the minimum required service conductor size is 4 AWG copper or 2 AWG aluminum. Using two 100-amp SEU cables, each rated for 100 amps, does not meet the minimum ampacity requirement for a 200 amp service.3.
Improper Bonding: The neutrals and grounds should be bonded together only at the service panel. Bonding them at multiple locations can create ground loops and potential electrical hazards.This practice was never common and has always been a code violation. It is essential to have the electrical system inspected and corrected by a qualified electrician to ensure safety and compliance with current electrical codes. Flag for review