Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Grounded Conductor Brought to Service Equip.

User: ron, Location: New York, 40.7514,-73.9925

Asked on: Friday, February 18, 2011 at 10:36 am EST
Answered on: Tuesday, May 14, 2024 at 1:46 am EDT

Question: 4 wire standby generator output and Y utility service is brought to a 3 pole XFER switch per 250.24(C). Does the XFER switch need to specified as 4 wire so there is an official place to terminate the grounded conductors?Since the gen and utility will have a N-G bond at each source making them separately derived systems, does the ATS need to be 4 pole per 250.20(D) even though there are no 4 wire loads?

Transfer Switch Wiring

Yes, the transfer switch should be specified as 4-wire to provide an official place to terminate the grounded conductors from both the generator and utility sources. This is required by Article 250.24(C)(1) of the National Electrical Code (NEC), which states that "Where a separately derived system is connected to a ground-fault protection system, the grounding electrode conductor or equipment grounding conductor for the separately derived system shall be connected to the grounding electrode conductor or equipment grounding conductor for the other system(s) at the service."

Transfer Switch Poles

According to NEC 250.20(D), a transfer switch for a separately derived system must have a "sufficient number of poles to disconnect all ungrounded conductors and the grounding electrode conductor or equipment grounding conductor." In this case, since both the generator and utility are separately derived systems and there are no 4-wire loads, a 3-pole transfer switch is sufficient.

Summary:
The transfer switch should be specified as 4-wire to terminate the grounded conductors. A 3-pole transfer switch is sufficient for this application, as there are no 4-wire loads. Flag for review

Previous Question Next Question