Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: sizing GEC for dual conductors

User: Steviechia2, Location: Massachusetts

Asked on: Friday, February 18, 2011 at 11:54 am EST
Answered on: Tuesday, May 14, 2024 at 1:46 am EDT

Question: I have 2 sets of 750 mcm conductors and am trying to figure my egc sizing. I'm on table 8 and I forgot which column I have to look at. I believe it's the stranding, diameter column? this would put me with a 3/0 copper conductor

Yes, on Table 8 of the NEC, you should look at the "Stranding, Diameter" column to determine the equivalent grounding conductor (EGC) size for 750 MCM conductors.The table shows that 750 MCM conductors have a stranding of 37 x 0.192 inches. The column corresponding to this stranding is "1/0-3/0", which indicates that a 3/0 copper conductor should be used as the EGC. Flag for review

Previous Question Next Question