Topic: Main distribution feed..120/208v 2000amp

User: ivan palacios, Location: Tennessee

Asked on: Friday, February 18, 2011 at 7:16 pm EST
Answered on: Tuesday, May 14, 2024 at 1:47 am EDT

Question: The prints are calling for (8) 4in. schedule 40 pvc pipes. Wire size is 500 kcml with a 500 kcml Equipment Ground (yes i know overkill) A vault will be set as a juction where the wire will make a 90 degree turn. I need to find the calculation for the minimum size vault. How do i go about this? Thank you.

Step 1: Calculate the Total Conduit Cross-Sectional Area For 4-inch Schedule 40 PVC pipes, the inside diameter is 3.826 inches. The cross-sectional area for each pipe is: π(3.826/2)^2 ≈ 11.47 square inches. Total cross-sectional area for 8 pipes: 8 x 11.47 = 91.76 square inches.

Step 2: Convert Wire Size to Cross-Sectional Area
500 kcmil copper wire has a cross-sectional area of approximately 0.31 square inches. Total cross-sectional area for 3 wires (2 phases + 1 equipment ground): 3 x 0.31 = 0.93 square inches.

Step 3: Calculate the Minimum Vault Size
The minimum vault size should be large enough to accommodate the following clearances: 6 inches of clearance around all conduits and wires for working space. 2 inches of clearance between parallel conduits or wires. The vault depth should be at least 24 inches.

Step 4: Calculate the Vault Dimensions
Assume the vault is a rectangular prism with a rectangular base. Let L be the length, W be the width, and D be the depth of the vault (in inches). From the clearances, we have: L ≥ 8 x (3.826 + 6) + 0.93 + 6 = 68.18 inches W ≥ 2 x (3.826 + 6) + 0.93 + 6 = 30.93 inches D ≥ 24 inchesStep 5: Choose the Vault Size Based on the calculations, the minimum vault size is approximately 68.18 inches long, 30.93 inches wide, and 24 inches deep. To provide additional space for future expansion or maintenance, it is recommended to round up the dimensions to the nearest standard size: Length

72 inches

Width

36 inches


Depth

30 inchesTherefore, the recommended minimum size for the vault is

72 inches long, 36 inches wide, and 30 inches deep
. Flag for review