Topic: Firestopping

User: electricgolfnut, Location: MA

Asked on: Friday, February 18, 2011 at 8:17 pm EST
Answered on: Tuesday, May 14, 2024 at 1:47 am EDT

Question: Is there a code requirement for this or is it building code or both? I am told that thru fire rated wall it must always be done.Great Forum...Mikey the man!!!

National Electrical Code (NEC) Article 300.21(C) requires that raceways passing through fire-rated walls be sealed with approved materials to maintain the fire-resistance rating of the wall.

International Building Code (IBC)
Section 714.3 requires that openings in fire-rated walls be protected in accordance with approved methods, such as sealing with listed materials.

NFPA 101: Life Safety Code* Section 7.2.
1.6
requires that openings in fire-rated walls be sealed with materials that maintain the fire-resistance rating of the wall.

Both building codes and electrical codes require raceways passing through fire-rated walls to be sealed with approved materials. This requirement helps to prevent the spread of fire and smoke through openings in fire-rated walls. Flag for review