Asked on: Friday, February 18, 2011 at 9:06 pm EST
Answered on: Tuesday, May 14, 2024 at 1:47 am EDT
Question: I have the following questions on this code section and how it applies to Hospital Grade MC cable.1. Can the hospital grade MC be used in branch circuits in patient care areas or does (1) limits you to hard pipe?2. If the answer to the above question is "NO" than is it acceptable to hard pipe within a patient care area and set a j-box outside it (say in a corridor) and MC a homerun back to the panel?3. Does this code section apply to feeders routed in "feeder type" MC cable? In other words if a feeder passes thru a patient care area to get to a panelboard, is hard pipe required as it is not a "branch circuit".4. In the definitions of 517, how does patient care vancinity correlate with patient care area? Would lighting in a patient care area be exempt because its is above the 7'-6" height indicated in the definition of patient care vacinity?Any input is greatly appreciated!
1. Can hospital grade MC be used in branch circuits in patient care areas or does (1) limits you to hard pipe?
Yes, hospital-grade MC cable can be used in branch circuits in patient care areas under certain conditions.2. If the answer to the above question is "NO" than is it acceptable to hard pipe within a patient care area and set a j-box outside it (say in a corridor) and MC a homerun back to the panel?
This is not necessary. Hospital-grade MC cable can be used in branch circuits in patient care areas when installed in accordance with the requirements of Article 517.3. Does this code section apply to feeders routed in "feeder type" MC cable? In other words, if a feeder passes through a patient care area to get to a panelboard, is hard pipe required as it is not a "branch circuit".
Yes, the requirements of Article 517 apply to both branch circuits and feeders.4. In the definitions of 517, how does patient care vicinity correlate with patient care area? Would lighting in a patient care area be exempt because its is above the 7'-6" height indicated in the definition of patient care vicinity?
Patient care vicinity is defined as the space within a patient care area and up to a distance of 6 feet (1.8 m) outside the edge of the patient care area. Patient care areas are defined as areas intended for the examination, diagnosis, treatment, or care of patients. Lighting in a patient care area would not be exempt if it is within the patient care vicinity. Flag for review