Question: Just something I saw recently, 3 phase 480v service disconnect feeding a panelboard with 2-500kcmil and 1-350kcmil on phase b all fused at 250a. was use-2 alum feeder wire, can you even do this?
Can you install 2-500kcmil and 1-350kcmil USE-2 aluminum feeder wires on a 3-phase, 480V service disconnect fused at 250A?Yes, it is possible to do this according to the National Electrical Code (NEC).NEC Requirements
Section 310.15(B)(16)
Aluminum conductors shall not be used in sizes smaller than 8 AWG, except as permitted in 310.15(B)(17) and 310.15(B)(18).
Section 310.15(B)(17)
Aluminum conductors may be used for feeders if they are at least 500 kcmil copper-clad or 750 kcmil bare or covered.
Section 310.16
The ampacity of the conductors must be sufficient for the load.
Section 240.21
The overcurrent protective device (fuse) must be rated at or below the ampacity of the conductor.
Conductor Ampacity
According to Table 310.16 in the NEC, the ampacity of USE-2 aluminum conductors is as follows: 500 kcmil: 375A 350 kcmil: 290A
Fuse Rating
The fuse rating is 250A, which is less than the ampacity of the 500 kcmil conductors. Therefore, the fuse rating is acceptable.
Conclusion:
Based on the NEC requirements, it is permissible to install 2-500 kcmil and 1-350 kcmil USE-2 aluminum feeder wires on a 3-phase, 480V service disconnect fused at 250A. Flag for review