Question: When installing MC or NMC through bored holes in BCI joist or any typ of wood framing is there a NEC or BC code or chart/table to how many cables you can fit in all different size bored holes,
NEC Article 330.14(A)(1): Cables installed through bored holes in studs, joists, or rafters shall be protected from physical damage by bushings or grommets installed at the edges of the holes. Article 330.14(A)(2): The diameter of the hole through which the cable is installed shall not be more than 1 inch for cables rated up to and including 4 AWG, or not more than 1-1/4 inches for larger cables.
IBC
The IBC does not provide any specific requirements for the installation of cables through bored holes in BCI joists or other types of wood framing.
NFPA 70E* Section 110.3(B): Electrical installations shall be made in accordance with the NEC.
Charts/Tables
The NEC Handbook provides the following chart (Table 330.14) for the maximum number of cables that can be installed through bored holes in studs, joists, or rafters:| Nominal Inside Diameter of Hole (inches) | Maximum Number of Cables
| ---|---|--- |
| 3/4 | 2 |
| 1-1/4 | 6 |
| 1-3/4 | 10 |