Topic: Connecting to a junction box extension ring

User: badashuka, Location: Miami Fla.

Asked on: Saturday, February 19, 2011 at 7:06 pm EST
Answered on: Tuesday, May 14, 2024 at 1:48 am EDT

Question: Can you connect to a J box using the knock outs on a extension ring? Please direct me to the code

Yes, you can connect to a J box using the knockouts on an extension ring.National Electrical Code (NEC) Article 314.24(A)(2) - "Outlet boxes, junction boxes, and similar enclosures shall be securely fastened in place. They shall be supported in accordance with 314.23(G)." Article 314.25(B) - "Flush-type boxes and extensions of surface boxes shall be installed so that the front edge of the box is flush with the finished surface." Article 314.27(A) - "Boxes used as junction boxes shall be provided with a volume that is adequate for the number of conductors contained in the box."Additional Considerations: The extension ring must be listed for use with the J box. The knockouts on the extension ring must be compatible with the size and type of conduit used. The conductors must be properly terminated in the J box and extension ring.* The connection between the extension ring and the J box must be made using approved methods, such as locknuts or listed connector fittings. Flag for review