Question: Hello,I have a building of 8 appartments with 100A Panelboard for each appartment. Each panel is fed by 50 mm2 cable from a main distribution board which is around 50 meter away from the building. So 8 cables are coming into the building.What is the enough size for a grounding ring cable that will go around the building? Following 250.66 will 25 mm2 of cable ring around the building be enough?Is following 250.52(A)(4) minimum conductor size of 2 AWF is a must in this case?Same question for another building with 59 appartments + 59 panels + 59 Feeders of 50 mm2 for each appartment? what would be the minimum size here?Many thanks
Building with 8 Apartments Grounding Ring Size
Yes, 25 mm² copper cable would be sufficient for the grounding ring around the building as per 250.66.
Conductor Size (2 AWF)
Yes, a minimum conductor size of 2 AWF (13.3 mm² copper) is required for the grounding conductors per 250.52(A)(4). This is more stringent than the requirement for the grounding ring size.
Building with 59 Apartments Grounding Ring Size
Based on 250.66, the minimum size for the grounding ring would be: 2 conductor size (13.3 mm²) for buildings with 10-50 dwelling units 3 conductor size (25.3 mm²) for buildings with 51-100 dwelling units
Conductor Size (2 AWF)
Again, the minimum conductor size for the grounding conductors per 250.52(A)(4) is 2 AWF (13.3 mm² copper), which is the more stringent requirement.
Recommended Conductor Size
In both cases, it is recommended to use a conductor size that is at least equal to the feeder conductor size (50 mm²). This will ensure proper grounding in the event of a fault. Therefore, for both buildings, the recommended grounding ring conductor size is 50 mm² copper. Flag for review