Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Branch Circuit to Light on Tree

User: czars, Location: West Melbourne, FL

Asked on: Sunday, February 20, 2011 at 3:38 pm EST
Answered on: Tuesday, May 14, 2024 at 1:50 am EDT

Question: 2008 NEC, Article 225.26 states that trees can't be used to support overhead conductors. However, I can't find a code article that permits or prohibits using a tree to support a branch circuit and an associated outside light. What am I missing?

2008 NEC Reference

Article 225.26(A)(1): "Open conductors shall not be attached to buildings or trees." Article 225.26(B)(3): "EXCEPTIONS: [...] (f) Conductors supported by messenger supported by a messenger attachment on a pole or other support."

Interpretation

The 2008 NEC

prohibits
attaching open conductors to trees in general (225.26(A)(1)). However, there is an exception that allows conductors to be supported by a messenger attached to a pole or other support (225.26(B)(3)(f)).In the case of a branch circuit and outside light, the conductors are typically run in a cable (e.g., UF or MC cable) that is supported by a messenger wire. The messenger wire can be attached to a pole, building, or other support, but not to a tree.

Conclusion:

The 2008 NEC does not specifically prohibit using a tree to support a branch circuit and outside light, but it does prohibit attaching open conductors to trees. Therefore, you must use a cable and messenger wire to support the conductors, and the messenger wire must be attached to a pole, building, or other support, not a tree. Flag for review

Previous Question Next Question