Question: We are installing a 200kva ups unit. We are transferring 3 ckts from the existing gear and feeding it off of the ups. Our downtime is extremely limited due to the nature of the loads. My original plan was to splice the new conductors from the ups with the existing conductors located in the switch gear.My boss brought up 408.3(3). Are there any exceptions to this section? The alternative is to install a junction box above the gear and remove the existing feeders and splice in the box, however, this will increase the downtime significantly. Any ideas are greatly appreciated.
Exception to NEC 408.3(3)
NEC 408.3(3) typically prohibits splices within enclosures for lighting fixtures and appliances, but there is an exception that allows splices in enclosures for commercial power conditioning equipment:> Exception for Commercial Power Conditioning Equipment. In addition to the requirements in 408.3(2), splices shall be located within a listed enclosure designed for the purpose or within an approved enclosure provided for the purpose.This exception applies to enclosures for commercial power conditioning equipment, including UPS units.
Recommended Solution
Based on the exception, you can splice the new conductors from the UPS unit to the existing conductors within the enclosure of the UPS unit. This will minimize downtime and meet the requirements of NEC 408.3(3).
Additional Considerations
Use proper splicing techniques and materials, such as wire nuts or heat shrink connectors. Label the splices clearly for future maintenance. Ensure that the UPS enclosure is suitable for the number and size of splices being made. Coordinate with the UPS manufacturer for any specific instructions or requirements.
Junction Box Option
Installing a junction box above the gear will increase downtime, but it may be a more convenient option if the UPS enclosure is not suitable for splicing or if there are other limitations. In this case, you would remove the existing feeders from the switchgear, install the junction box, and splice the new conductors from the UPS unit to the existing conductors within the junction box. Flag for review