Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Demand Factors Hotel

User: Artemis, Location: DC area

Asked on: Monday, February 21, 2011 at 2:13 pm EST
Answered on: Tuesday, May 14, 2024 at 1:51 am EDT

Question: Looking for some help on demand factors for a hotel. A 41 room 2 story with water heater (4500 W) and a thru wall HVAC unit (5000 W) in each room. Used the tables in Article 220 for lighting and receptacles. When calculating the service I am at 24.3 VA/sf. An elevator and fire pump are the only large motors in the building. What am I missing?

Non-Linear Loads

Modern electronics (e.g., televisions, computers, chargers) create harmonic distortion, which increases the apparent power (VA) requirement. Consider a 20% non-linear load factor.

Diversity Factor

Not all loads will be operating at their maximum capacity simultaneously. Use a diversity factor to reduce the calculated load. A typical value for hotels is 0.75.

Corrected Demand Load

Corrected Demand Load = Calculated Demand Load x Non-Linear Load Factor x Diversity Factor

Lighting Demand

1000 VA/sf for general lighting (from Table 220.12(A)) 150 VA/sf for guestroom lighting (from Table 220.12(B))

Receptacle Demand

250 VA/sf for general receptacles (from Table 220.12(A)) 100 VA/sf for guestroom receptacles (from Table 220.12(B))

Water Heater and HVAC

Include the connected load of the water heater and HVAC units in the total demand calculation.

Large Motors

Calculate the starting and running currents for the elevator and fire pump motors. Multiply by voltage to obtain the VA demand.

Recalculated Service Demand

Using the above considerations, recalculate the service demand:
Corrected Demand Load = 24.3 VA/sf x 1.2 (non-linear factor) x 0.75 (diversity factor) = 21.9 VA/sf Lighting Demand = 1000 VA/sf + 150 VA/sf = 1150 VA/sf Receptacle Demand = 250 VA/sf + 100 VA/sf = 350 VA/sf Water Heater Demand = 4500 W = 4500 VA HVAC Demand = 41 rooms x 5000 W = 205,000 W = 205,000 VA Elevator Demand (assuming 50 hp) = 50 hp x 746 W/hp = 37,300 W = 37,300 VA Fire Pump Demand (assuming 100 hp) = 100 hp x 746 W/hp = 74,600 W = 74,600 VATotal Demand = 21.9 VA/sf x 6600 sf (hotel area) + 4500 VA + 205,000 VA + 37,300 VA + 74,600 VA = 370,000 VA

Therefore, the service should be sized for 370,000 VA.
Flag for review

Previous Question Next Question