Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Grounding Halo

User: Richard Cummins, Location: Chattanooga TN

Asked on: Monday, February 21, 2011 at 3:05 pm EST
Answered on: Tuesday, May 14, 2024 at 1:51 am EDT

Question: We currently use a grounding Halo made up of 2 1/2" x 1/4" x 10' section of bus bar. We connect all MCC's and Swithgear on both ends of the gear with a 4/0 AWG cable to the grounding Halo. We ground all other metal surfaces to the Halo with the appropriate sized grounding conductor. We use a pressure lug on the cable and bolt the lug to the grouinding Halo. We ground the Halo with a 4/0 AWG cable to the metal base of our building's Stainless Steel ground pad with a lug on each end. I have had an electrical inspector tell me that the connections to the grounding Halo are considered splices NEC 250.64 (C) (1) and I need to use a non reversible connection means to the grounding Halo and ground pad. We use a 3/8" bolt with a flat washer on both sides and a compression washer before the 3/8 nut. What is your opinion?

NEC Requirements

NEC 250.64(C)(1) states that splices in a grounding conductor shall be made with approved splicing devices or by the brazing, welding, or soldering of conductors.

Interpretation

The inspector's interpretation that the connections to the grounding halo are considered splices is reasonable. The use of pressure lugs and bolts to connect cables to the halo could be considered a form of splicing.

Non-Reversible Connection Means

NEC 250.64(D) requires that grounding conductors shall be connected to the grounding electrode system with a non-reversible connection means.The use of a 3/8" bolt with washers and a compression washer could be considered a non-reversible connection means. However, it is important to ensure that the compression washer is properly installed and tightened to create a secure and permanent connection.

Recommendation

Based on the NEC requirements and the inspector's interpretation, it is recommended to modify the connections to the grounding halo and ground pad to meet the following criteria: Use an approved splicing device or method for connections to the grounding halo. This could involve using splicing kits or compression connectors designed for grounding applications. Ensure that the connections to the grounding electrode system (ground pad) are made using a non-reversible connection means. This could involve using compression connectors, welding, or soldering.

Additional Considerations The size and type of grounding conductor used should be appropriate for the fault current and grounding system design. The grounding connections should be inspected and maintained regularly to ensure that they remain tight and secure.* It is always advisable to consult with a qualified electrician for specific guidance and code interpretation. Flag for review

Previous Question Next Question