Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Sizing Disconnects for motors

User: wmeek, Location: Texas

Asked on: Monday, February 21, 2011 at 5:51 pm EST
Answered on: Tuesday, May 14, 2024 at 1:51 am EDT

Question: When sizing a disconnect for a motor do you use the Table amps in the code or do you use the nameplate. I have a 20HP 3Phase motor at 240V. The table Amps is 54A. So 54 x 115%= 62.1A. Can you go down to a 60A or go up to a 100A Nonfusible disconnect General duty safety switch.

Sizing Disconnect

For sizing the disconnect for a motor, you should typically use the nameplate current rating of the motor, not the table amps from the code.

Calculation Using Nameplate Data

Motor HP: 20 HP Voltage: 240 V (3-phase)Using the formula:

Line Current (A) = (HP x 746) / (Voltage x 1.732 x Efficiency)
Assuming an efficiency of 85%:
Line Current = (20 x 746) / (240 x 1.732 x 0.85) = 56.7 A


Disconnect Size

Based on the calculated line current of 56.7 A: A 60 A disconnect would be too small (below the required 115% of line current, which is 65.04 A). A 100 A disconnect would be acceptable and provide ample capacity.

Conclusion

For a 20HP motor at 240V, you should choose a

100A Nonfusible disconnect General duty safety switch.
Flag for review

Previous Question Next Question