Question: I checked out a job today and I need to wire up a 16kw Generator for the homeowner.The run is 125' total including the wire needed outside to the generator if I go diagonal through the web joists in his basement. The breaker on the generator is 65A and the transfer switch/panel calls for a 70A breaker.Can I run a 4-4-4-6 AL SER for the main power, or does it need to be a 2-2-2-4 AL SER?He wanted all copper conductors and it would cost him a fortune if I had to run pipe and THHN the whole way because the run would be longer.If I end up drunning SER would I be able to put a junction box inside, strip the SER back and run it in pipe from the J-Box to the Generator(About 12 feet)?Also What would you guys suggest for running the four control wires?Small FMC through the joists to the J-box?Please excuse my ignorance, I just want to make sure I'm goign to do this right and I'm rusty on residential.Thanks!-Ian

Generator Wiring

The appropriate wire size for a 16kW generator with a 65A breaker is 2-2-2-4 AL SER. You cannot use 4-4-4-6 AL SER for the main power.

Conduit vs. SER

You can use a junction box inside the basement and run the SER in conduit from the junction box to the generator. However, you must use a listed conduit fitting to transition from the SER cable to the conduit.

Control Wires

To run the four control wires, you can use small FMC (flexible metal conduit) through the joists to the junction box. FMC is an approved method for protecting wires from damage.

Recommended Wire Sizes



Main Power

2-2-2-4 AL SER


Control Wires

14 AWG THHN (if using FMC) or 12 AWG THHN (if running directly through web joists)

Installation Notes:
Make sure to follow the manufacturer's instructions for the generator and transfer switch. All electrical connections must be properly made and secured with approved connectors. Use ground rods and bonding straps as required by code. Obtain the necessary permits and have your work inspected by a qualified electrician before connecting the generator to the electrical system. Flag for review