Topic: 3-phase 208V Wye to 240V Delta w/ common center taps

User: dindremr, Location: Wisconsin

Asked on: Monday, February 21, 2011 at 8:13 pm EST
Answered on: Tuesday, May 14, 2024 at 1:51 am EDT

Question: We have a hot tub retailer in a new tenant space in a building with a 3-phase 208V Wye service. Their show room hot tubs require 240V split-phase (center tap neutral - standard 1-phase power). We have proposed 3 - 208 to 240 isolation transformers with the center taps of each connected to the service neutral. Question is - can the H1s be connected to the adjacent transformers' H3s to form a Delta configuration and feed a single 3-phase panel (the preferred approach) OR must the high outputs of the transformers remain isolated and feed 3 independent 1-phase panels (the default approach)? My phasor diagram indicates it should be OK, however this is in no way a common configuration making me think there be an issue. I appreciate your feedback and welcome an explaination as to why the delta configuration will not work.

Connecting the H1s of the adjacent transformers to the H3s to form a Delta configuration and feed a single 3-phase panel is not allowed and would be a violation of the National Electric Code (NEC).

Reason

In a Delta configuration, the three H1 terminals are connected together to form a closed loop. The three H3 terminals are also connected together to form a closed loop. The neutral is not connected to either loop. In this configuration, the line-to-line voltages are 240V, but the line-to-neutral voltages are only 140V.However, the hot tubs require 240V split-phase power, which means that the line-to-neutral voltage must be 240V. In a Delta configuration, the line-to-neutral voltage is only 140V, which is not sufficient to power the hot tubs.

Correct Approach:


The correct approach is to use the three isolation transformers to provide 240V split-phase power to three independent 1-phase panels. Each panel will be connected to one of the transformers, and the neutral from the service will be connected to the center tap of each transformer. This will provide 240V line-to-neutral voltage to each panel, which is what the hot tubs require. Flag for review