Question: Question A: Can the main overcurrent protection device (OCPD) of a panel fed by the secondary conductors of a transfomer be considered the secondary protection for the transformer?Question B: Can a primary fuse that is NOT connected directly to the primary terminals of the transformer (but connected to it through a cable) qualify as primary protection?Just to clarify my quuestion.1. I am not asking about conductor protection.2. I am not asking if the primary or secondary OCPD is properly sized.3. I am asiking if the fuse in the primary side of the transformer qualifies as a primary OCPD even though it is not cnnected directly to the terminals of the transformer and this fuse is part of a feeder circuit of the upstream panel.4. I am asking if the main OCPD for the downstream panel conected to the transformer qualifies as a secondary OCPD for the transformer even though it is not connected directly to the secondary terminals of the transformer but there is a cable between the transformer secondary and the main OCPD for the downstram panel.Thanks.
Answer A
NoNEC 450.3 requires that a primary fuse or circuit breaker be installed on each transformer. The secondary protection cannot be considered the primary protection.
Answer B
NoNEC 450.3 requires that the primary fuse or circuit breaker be connected directly to the transformer primary terminals. A fuse connected through a cable does not meet this requirement.
Additional Clarification
Conductor Protection
The main OCPD in the downstream panel does not provide protection for the secondary conductors of the transformer. The transformer secondary conductors must be protected by a secondary OCPD installed in the same enclosure as the transformer.
OCPD Sizing
The primary and secondary OCPDs must be sized according to the requirements of NEC 450.5 and NEC 450.6, respectively.
Primary OCPD Location
The primary OCPD must be installed in a readily accessible location as close as practicable to the transformer.
Secondary OCPD Location: The secondary OCPD must be installed as part of the secondary circuit and must be rated for the maximum circuit current. Flag for review