Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 2 services or 2 Feeders? Ur input needed

User: bran82004, Location: WISCONSIN, USA

Asked on: Monday, February 21, 2011 at 11:06 pm EST
Answered on: Tuesday, May 14, 2024 at 1:52 am EDT

Question: running into a problem... have an exsiting tenent space in a small strip mall. underground service lateral comes into the mech room into the utility providers CT cabinet. off of the cabinet it splits off and feeds 6 main disconnects. question is does 225.30 prevent us from using 2 of the 200 amp mains to feed this one tenant space? the building only has the one service supply, and to prevent an expensive upgrade to a 400 amp feeder could we use 2 seperate feeds?

NEC Interpretation

Section 225.30 of the National Electrical Code (NEC) does not specifically prohibit dividing the service into multiple feeds for a single tenant space.

Code Requirements

However, it's important to consider other relevant NEC requirements:

Article 225 Service Overcurrent Protection

The service overcurrent protective devices (main disconnects) must be rated to protect the service conductors.


Article 210 Branch Circuits

Branch circuits cannot exceed the maximum ampacity of the conductors and overcurrent protection devices.

Article 220 Branch-Circuit and Feeder Calculations

The load calculations must determine the necessary ampacity of the feeder and branch circuits.

Feasibility of Splitting Service

Given the limited information provided, it's feasible to split the service into two 200-amp feeds for the following reasons:


Sufficient Ampacity

Two 200-amp feeders would provide ample ampacity for most tenant spaces.

Protection

The two main disconnects would provide overcurrent protection for the separate feeders.


Branch Circuit Capacity

The branch circuits can be sized appropriately to match the connected loads.

Recommendations

Before implementing this solution, it's advisable to:

Consult with Inspector

Discuss the proposed solution with the local electrical inspector to obtain their approval and guidance.


Load Calculations

Perform thorough load calculations to ensure that the two 200-amp feeders will be sufficient for the expected electrical loads.

Conduit Size

Verify that the existing conduit can accommodate the two 200-amp feeders.


Short Circuit Current

Ensure that the two feeders are properly coordinated with respect to short circuit current.

Note:
It's important to ensure that the two feeders are properly labeled and segregated to prevent accidental overloading of either feeder. This solution may not be suitable for all tenant spaces, especially those with high electrical loads. Flag for review

Previous Question Next Question