User: suemarkp, Location: Kent, WA
Asked on: Monday, February 21, 2011 at 11:13 pm EST
Answered on: Tuesday, May 14, 2024 at 1:52 am EDT
Question: I'm looking for information specific to Washington state. I think this state adopted some portions of NEC 90.7 of the NEC requiring that all electrical utilization equipment sold or installed in WA be listed by a WA recognized testing laboratory. For many items, this is fine. However, we have labs containing electrical items that were designed for airplanes (never listed for premises use), or custom things we put together ourselves such as power distribution for that equipment (mostly this is just adapting connectors to power supplies of 28V and 400 Hz).Does anyone know the true scope of this (utilization equipment can be interpreted to be about anything), and whether things we build to use locally (not for sale) need to be NRTL tested? Is this really an OSHA thing? How much leeway does NEC 590.3(C) give us, as this equipment goes in development and testing labs? Finally, if you take a bunch of UL listed equipment and install it in an equipment rack, have you ever heard of anyone saying you've changed the equipment and the whole rack must now be NRTL tested as an assembly?
Washington Administrative Code (WAC) 296-46B-380 adopts NEC 90.7, which requires electrical utilization equipment sold or installed in Washington to be listed by a Washington recognized testing laboratory (WRTL).
Scope of the Requirement
The requirement applies to all electrical utilization equipment, including: Equipment that is built, designed, or adapted for installation within a building Equipment that is used in or on buildings for industrial or commercial purposes Equipment that is not intended for use in or on buildings, but is temporarily installed for testing, maintenance, or repair
Local Use Exemption
NEC 590.3(C) provides an exemption for equipment that is not sold or installed elsewhere. However, this exemption only applies if the equipment is: Manufactured for use only within the laboratory Not intended for sale or installation outside the laboratory Installed in accordance with NEC requirements
NRTL Testing for Custom Equipment
If you are building custom equipment for use in your laboratory, it should be designed and tested to meet applicable NEC requirements. However, it is not necessary to have it NRTL tested unless it is intended to be sold or installed outside the laboratory.
OSHA Applicability
NEC 90.7 is not an OSHA requirement. However, OSHA does require employers to provide a safe work environment, which includes ensuring that electrical equipment is properly installed and maintained. Therefore, OSHA may cite an employer for using electrical equipment that does not meet applicable NEC requirements.
Assembly Testing
Installing UL listed equipment in an equipment rack does not typically require the entire assembly to be NRTL tested. However, if the installation involves any modifications to the UL listed equipment, or if the assembly is intended to be marketed as a new product, NRTL testing may be required.
Specific Questions for Washington:
For specific questions about the application of WAC 296-46B-380, it is advisable to contact the Washington State Department of Labor & Industries (L&I): Phone: (360) 902-5490 Email: [[email protected]](mailto:[email protected]) Flag for review