Question: Can anybody give me a good explanation on why interrupting ratings on breakers will vary from one application to the next? For example on a 800 amp MB Disconnect the trip rating is 50K @ 480v. On a 150 amp feeder breaker the rating is at 35K, and on a motor control bucket the rating is 65KA (instantaneous). (These are all specs from an Allen Bradley MCC) What do these ratings mean and how do you go about deciding which application is right for your particular task?
Interrupting Rating (IR)
The interrupting rating of a breaker is the maximum amount of current that it can safely interrupt in the event of a fault. This rating is expressed in kiloamperes (kA).
Factors Affecting Interrupting Rating
The interrupting rating of a breaker is affected by several factors, including: Voltage
The higher the voltage, the lower the interrupting rating.
Frequency
The higher the frequency, the lower the interrupting rating.
Current level
The higher the current level, the lower the interrupting rating.
Breaker design
Different breaker designs have different interrupting ratings.
Arc extinguishing medium
The type of arc extinguishing medium used in the breaker can also affect the interrupting rating.
Application-Specific Interrupting Ratings
The interrupting rating required for a particular application depends on the following factors: Circuit conditions
The voltage, current, and fault current level on the circuit.
Equipment protection
The interrupting rating must be sufficient to protect the equipment connected to the circuit.
Personnel safety
The interrupting rating must be sufficient to ensure the safety of personnel working on or near the circuit.
Rated Interrupting Capacity Chart
A rated interrupting capacity (RIC) chart is a table that provides the interrupting rating of a breaker for different circuit conditions. This chart is typically provided by the breaker manufacturer.
Selecting a Breaker
To select a breaker for a particular application, you need to determine the following: Circuit conditions
The voltage, current, and fault current level on the circuit.
Equipment protection
The type of equipment connected to the circuit and the protection required.
Personnel safety
The location and accessibility of the circuit.Once you have determined these factors, you can consult the RIC chart to select a breaker with an interrupting rating that meets or exceeds the requirements.
Example MB Disconnect (800A)
50kA @ 480V
Feeder Breaker (150A)
35kA
Motor Control Bucket: 65kA (instantaneous)In this example, the MB disconnect has the highest interrupting rating because it is connected to a higher voltage and amperage circuit. The feeder breaker has a lower interrupting rating because it is connected to a lower voltage and amperage circuit. The motor control bucket has an instantaneous interrupting rating, which means it trips almost immediately in the event of a fault. Flag for review