Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Load on Grounding Conductor

User: jbolen, Location: NE (9.06 miles @5.9 Degrees from Winged Horses)

Asked on: Tuesday, February 22, 2011 at 1:57 am EST
Answered on: Tuesday, May 14, 2024 at 1:52 am EDT

Question: I have two parallel 4/500 with 2 1/0 grd cables each feeding a 120/208 3 phase feeding an 800 AMP MDP.During maintenance check found 26 amps on grounding condutors going back to the Generator. The main bonding jumper is a 4/0 from ground bar to neutral bar in MDP with 4/0 grd loop with five grd rods.Question why would I have a load of 26 amps on ground and only 10 amps on the 500 mcm neutral.Lost in Afghansitan.

Possible Reasons for High Ground Current and Low Neutral Current



Inductive Load

Electric motors, transformers, and other inductive loads can create unbalanced current in the system, causing higher ground currents and lower neutral currents.


Equipment Fault

A ground fault in a piece of equipment downstream of the MDP can allow current to flow through the ground path instead of the neutral path.

Poor Neutral-Ground Bond

A loose or corroded neutral-ground bond in the MDP or elsewhere can increase ground current and decrease neutral current.


Open Neutral Conductor

A broken or disconnected neutral conductor can prevent neutral current from returning to the source, resulting in high ground currents.

Floating Neutral

In some systems, the neutral may be floating, meaning it is not connected to ground at the source. This can cause unpredictable ground current and low neutral current.

Steps to Troubleshoot

1.

Inspect Equipment

Check all connected equipment for ground faults or loose connections.2.

Verify Bonding

Ensure that the neutral-ground bond in the MDP and the grounding system is intact and properly sized.3.

Test Neutral Conductor

Use a continuity tester to ensure that the neutral conductor is continuous and free of breaks or disconnections.4.

Check for Floating Neutral

Measure the voltage between the neutral and ground terminals in the MDP. If the voltage is not zero, the neutral may be floating.5.

Install an Isolated Ground Monitor (IGM)

An IGM can detect and measure ground current, helping to identify the source of the imbalance.

Additional Considerations:
Ensure that the grounding system is adequately sized and has a low impedance path to ground. Use shielded cables or install ferrite cores on inductive loads to minimize common-mode noise that can contribute to ground current. Consider using a different grounding scheme, such as a corner-grounded delta system or a solidly grounded wye system. Flag for review

Previous Question Next Question