User: bkelly, Location: Ohio
Asked on: Tuesday, February 22, 2011 at 8:59 am EST
Answered on: Tuesday, May 14, 2024 at 1:53 am EDT
Question: This is a new installation of a fire pump in an existing building. The building has an attached transformer vault accessible from the outside. The engineer's drawings show to tap the secondary of the transformer in the vault, no OCPD or disconnecting means, and run a 2" GRC conduit through the ceiling app. 100' to the fir pump controller. the engineer spec's to use a fire resistant cable to meet the listing requirements of Circuit Conductors. I see these as service conductors, requiring to meet 695.6(A), thar requires them to be outside of the building.Anyone familliar with fire pumps that can offer some input? Thanks in advance.P.S. We are under 2008 NEC
The engineer's design appears to violate some of the requirements of the National Electrical Code (NEC) for service conductors. According to NEC 695.6(A), service conductors must be outside of the building or installed in raceways outside the building. In this case, the 2" GRC conduit running through the ceiling for 100' appears to be inside the building.Additionally, the NEC requires service conductors to be protected from physical damage by an overcurrent device (OCPD) and a disconnecting means. In this case, there is no OCPD or disconnecting means shown in the drawings.The fact that the engineer has specified a fire-resistant cable does not exempt the installation from the requirements of the NEC. Fire-resistant cables are designed to maintain circuit integrity during a fire, but they do not eliminate the need for overcurrent protection and disconnecting means.Based on the information provided, it appears that the engineer's design for the fire pump installation is not in compliance with the NEC. It is recommended that you discuss these concerns with the engineer and work together to find a compliant solution. Flag for review