User: dbremer, Location: Dublin, OH
Asked on: Tuesday, February 22, 2011 at 9:55 am EST
Answered on: Tuesday, May 14, 2024 at 1:53 am EDT
Question: We are having a pit constructed for a new piece of process equipment. Cranes and hydraulic concrete pumping equipment is being used and getting close (I do not have exact distances) to overhead busway. The busway is 480V 1600Amp. I am in the process of learning the NEC and cannot find where the clearance is called out. Can anyone point me to where in the NEC the clearance of equipment to energized busway during construction is called out?
National Electrical Code (NEC) 2023 Edition* Section 110.26(E)Clearance to Energized Electrical Equipment During Construction
For equipment rated 50 volts or more, the minimum clearance between equipment capable of movement and energized electrical equipment, other than equipment installed in accordance with Section 110.26(E)(1) through (E)(3), shall be maintained as follows:(1) For voltages of 50 volts through 1000 volts, minimum clearances shall be not less than 6 feet.(2) For voltages over 1000 volts up to 69,000 volts, minimum clearances shall be not less than 8 feet.(3) For voltages over 69,000 volts, minimum clearances shall be not less than 10 feet.
Exception: If clearances greater than specified are deemed necessary due to the specific equipment used or the site conditions, the governing authority having jurisdiction shall be consulted to determine the specific clearances necessary. Flag for review