User: Windadct, Location: Doylestown PA
Asked on: Tuesday, February 22, 2011 at 11:02 am EST
Answered on: Tuesday, May 14, 2024 at 1:53 am EDT
Question: Hello All:I have 8 spaces left in my 200 A panel and am adding a pool and finishing the basement. My initial thoughts were that I needed 4 Branch for Rcept and Lights in the basement, a 2 pole and single feed for the pool - 7 spots total needed.However my township is requiring that I heat my new space 850 Sq ft ~ 8500W so that will consume 2 x 2pole spots - and I have no room. Additionaly the new branch ckts require AFCI - the Inspector/Underwriter had to preapprove the plan prior to getting a Const Permit - the AFCI were explicitly called out.OK so my question is this - If I use a few Tandem 15 Breakers ( Siemens QP) to free up some spaces in the panel on existing branch circuits - is this technically a upgrade to my service? - and thus requiring them to be AFCI type ( no tandems available - i.e. pointless)Our Township is something known for being a PITA - however - for the cost of a few Tandems - I am tempted to give it a shot and if they flag it - well then deal with it then.( FYI - finishing basement for TV, craft and exercise - are you ready....Drylok poured concrete walls, R14 Insulation on exterior of finished spaces, Horiz Firestopping, Vert Firestop every 10 ft, 1KW heat per Sq ft, AFCI's, tamper proof Recept - in addtion to the usual Egress, and other construction standards.)Thanks -Paul
Technically, replacing existing breakers with tandem breakers is not considered an upgrade to your electrical service. However, since your municipality requires AFCI protection for new branch circuits, you may encounter issues if you install tandem breakers on circuits that do not currently have AFCI protection.Here's what can happen: Inspector disapproval
The building inspector may not approve your plan if you have tandem breakers without AFCI protection on circuits that require it.
Insurance issues
If you install tandem breakers without AFCI protection and there is an electrical fire, your insurance company may not cover the damages.*
Safety concerns: AFCIs help prevent electrical fires by detecting and interrupting arcing faults, which can be a potential fire hazard.To avoid potential problems, it's recommended that you use AFCI tandem breakers on all new branch circuits, even if you have to replace existing breakers to free up space in your panel.If you're concerned about the cost of AFCI breakers, you could consider using a subpanel to add additional circuit capacity to your home. This would allow you to install AFCI breakers on all new circuits without having to replace existing breakers.Ultimately, it's important to comply with all building codes and regulations in your area. Contacting the building inspector's office to clarify their requirements and discuss your options is the best way to ensure you meet all the necessary safety standards. Flag for review