User: PPerez, Location: Mission Viejo, CA
Asked on: Tuesday, February 22, 2011 at 2:13 pm EST
Answered on: Tuesday, May 14, 2024 at 1:54 am EDT
Question: I could use some help on a classification issue. We have a low pressure (30 psi max supply, reduced down to 1-2 psi at the blower unit) propane burner skid with two blowers, flow and pressure control intrumentation, and two burner heads. THe skid has a pressure relief vent at the blower units. NFPA 497 Fig 5.9.2(a) would appear to apply but the box in the figure shows that it is only applicable to medium or high pressure conditions. I can't find any reference or diagram for a low pressure condition.API RP 500 Fig. 14 and 18 show a 10' radius but the pressures referenced are nearly 300 psi.This is outdoors in an area with 10mph wind regularly and often times higher.Any advise? Do the pipe connections (flanges, valves, etc.) even qualify at these lower pressures? Is the system non-classified due to such low pressures?Thank you in advance.
## Classification for Low Pressure Propane Burner SkidBased on the information you provided, the low pressure propane burner skid falls under the following classification
Non-Classified
Reasoning
The NFPA 497 Fig 5.9.2(a) only applies to medium or high-pressure conditions, which your skid does not meet. Your skid operates at a maximum pressure of 30 psi, which is significantly lower than the high pressures referenced in API RP 500 Fig. 14 and 18.* At such low pressures, the potential for a flammable mixture to form is negligible.
Pipe Connections
The pipe connections (flanges, valves, etc.) on the skid do not qualify as classified components due to the low pressure conditions.
Conclusion:
Your low pressure propane burner skid is non-classified because it operates at low pressures where the risk of a flammable mixture is negligible. Therefore, the specific classification requirements from NFPA 497 and API RP 500 do not apply. Flag for review