User: laketime, Location: Tennessee
Asked on: Tuesday, February 22, 2011 at 2:46 pm EST
Answered on: Tuesday, May 14, 2024 at 1:54 am EDT
Question: Homeowner has a new 2 story house being built. They want 200amp panel/meter for each floor (going to rent one floor out). I am doing load calcs and for the one floor I have plans for a 200a is not over the top. Would I have to have a 400amp service drop to a dual meter pack and then break it down to (2) 200amps? Can you feed (2) 200amp panels off a 200amp drop?
Yes, it is possible to feed two 200-amp panels from a 200-amp service drop. This is done by using a subpanel.The service drop comes into a main panel, which is typically located on the exterior of the house. The main panel contains the main breaker, which is the largest breaker in the system and protects the entire electrical system.From the main panel, a feeder cable is run to a subpanel. The subpanel is located in the area where the additional power is needed, in this case, the second floor.The subpanel contains breakers that protect the individual circuits on the second floor. The subpanel is connected to the main panel by the feeder cable, which carries the power from the main panel to the subpanel.It is important to note that the total amperage of the breakers in the subpanel cannot exceed the amperage of the feeder cable. In this case, the feeder cable is 200 amps, so the total amperage of the breakers in the subpanel cannot exceed 200 amps.If the total amperage of the breakers in the subpanel exceeds the amperage of the feeder cable, the feeder cable will overheat and could cause a fire. Flag for review