Question: I was at a CE class today and the instructor stated that a sub panel in the same structure as the main that was feeding it needed a main breaker. He couldn't give a code reference but stated that a main lug panel would be a violation. I say he's wrong unless something changed.
Your instructor is correct.According to the 2020 National Electrical Code (NEC) Article 225.30, "Each subdistribution panelboard shall be provided with a main overcurrent protective device where the subdistribution panelboard does not contain a main circuit breaker."In other words, if a subpanel does not have a main circuit breaker, it must have a main overcurrent protective device, such as a main lug.Therefore, a main lug panel would be a violation in this case. Flag for review