User: philly, Location: Massachusetts
Asked on: Tuesday, February 22, 2011 at 4:57 pm EST
Answered on: Tuesday, May 14, 2024 at 1:54 am EDT
Question: If I recall there is a section in the NEC stating that for any breaker with an ampacity less than 100A you must use the 60deg C rating for determining cable ampacity for cables I believe up to size #1.Is this always the case, that you must use the 60deg column or if you know that the breaker terminals are rated for 75deg C then can you use the 75deg rating?
In the NEC, it states that for circuit breakers rated 100A or less, the 60°C rating must be used to determine cable ampacity for all conductor sizes. This applies to both copper and aluminum conductors.The 75°C rating may only be used if the manufacturer specifically states that the circuit breaker terminals are rated for 75°C. This information is typically found in the circuit breaker's technical data sheet or installation instructions.The reason for this requirement is that the 75°C rating is based on the assumption that the circuit breaker terminals will operate at a maximum temperature of 75°C. However, the terminals of circuit breakers rated 100A or less are typically not designed to withstand this high temperature, so they must be derated to the 60°C rating.By using the 60°C rating, you can ensure that the circuit breaker terminals will not overheat and fail. Flag for review