Topic: ATS Neutral connection for Utility and generator source

User: philly, Location: ORLANDO FLA

Asked on: Tuesday, February 22, 2011 at 5:14 pm EST
Answered on: Tuesday, May 14, 2024 at 1:54 am EDT

Question: Why do you need to have a 4-pole ATS when the ATS has its sources coming from both the utility and emergency generator both of which are solidly grounded? I believe it has something to do with the ATS breaker seeing less of a ground fault magnitude to interrupt the ground fault?

Yes, that is correct. A 4-pole ATS is required when the ATS has its sources coming from both the utility and emergency generator both of which are solidly grounded because the ATS breaker will see less of a ground fault magnitude to interrupt the ground fault.This is because when a ground fault occurs on the utility side of the ATS, the ground fault current will flow through the utility ground wire back to the utility transformer. This will create a low impedance path for the ground fault current, which will result in a high ground fault magnitude.However, when a ground fault occurs on the generator side of the ATS, the ground fault current will flow through the generator neutral wire back to the generator. This will create a high impedance path for the ground fault current, which will result in a low ground fault magnitude.The ATS breaker is designed to interrupt ground faults at a certain magnitude. If the ground fault magnitude is too low, the ATS breaker will not be able to interrupt the ground fault. This could result in a fire or other damage to the electrical system.By using a 4-pole ATS, the ground fault current will be divided between the two poles of the ATS breaker. This will result in a lower ground fault magnitude on each pole of the ATS breaker, which will make it more likely that the ATS breaker will be able to interrupt the ground fault. Flag for review

Previous Question Next Question