Topic: Utility Interactive Photovoltiac Inverters

User: marsac, Location: Utah

Asked on: Tuesday, February 22, 2011 at 10:11 pm EST
Answered on: Tuesday, May 14, 2024 at 1:56 am EDT

Question: Re: NEC 705.40 and NEC 705.42In our jurisdiction, we are encountering PV solar installations on 3-phase systems in which the PV inverter is a single phase production source.Our position is that both of the above code references requires a single phase PV source when attached to a 3-phase system to cease exporting power when the primary source loses one or all phases. This would include the phase that the single phase PV inverter is not connected to.We would appreciate your analysis and opinion.Thank you,

NEC 705.40

NEC 705.40(C) states that "Equipment shall be installed such that a loss of any one phase will not result in the failure of all output sources."This requirement is intended to prevent a single-phase fault from causing all of the output sources (PV inverters) on a three-phase system to shut down. This could result in a loss of power to critical loads.

NEC 705.42

NEC 705.42(B)(1) states that "Equipment shall be installed such that, in the event of a fault to ground on the inverter output, the inverter shall rapidly shut down."This requirement is intended to prevent a ground fault on the inverter output from causing a sustained flow of current to ground. This could result in a fire or shock hazard.

Analysis

In the case of a single-phase PV inverter attached to a three-phase system, a loss of any phase on the primary source (utility) would result in a loss of all output sources (PV inverters). This is because the PV inverter is not connected to the other two phases of the primary source.Therefore, a single-phase PV inverter attached to a three-phase system must be installed in a manner that ensures that it will cease exporting power when any phase of the primary source is lost. This can be accomplished by using a transfer switch or by connecting the PV inverter to a three-phase transformer.

Opinion

Your position is correct. NEC 705.40 and NEC 705.42 require a single-phase PV source when attached to a three-phase system to cease exporting power when the primary source loses one or all phases. This would include the phase that the single-phase PV inverter is not connected to. Flag for review