User: lonewolf454, Location: NE (9.06 miles @5.9 Degrees from Winged Horses)
Asked on: Wednesday, February 23, 2011 at 5:50 am EST
Answered on: Tuesday, May 14, 2024 at 1:56 am EDT
Question: My superior had the bright idea of replacing a hydraulic motor system with a VFD/motor combo. It is going to be a 3PH/460/50HP motor and PF700 75HP VFD. Problem is in the A-B book it calls for 100A breaker min for 75HP VFD. So I assume I will need not #4 AWG wire to VFD but instead #3. But that is recommended minimum. Per NEC, for 50HP (65FLA) motor, I calculate 81.25 for wire size, (#4) Fuse 113.75 (125A semiconductor) Breaker 162.5 (175A). Now if this breaker is to be 175A per NEC, then will I need to size wire from Breaker to VFD for 175A?I plan on #4 AWG from VFD to motor, but with larger VFD than needed, questions arise... Any suggestions?
Breaker and Wire Sizing
NEC
For a 50 HP motor with 65 FLA, you correctly calculated: Wire size: #4 AWG (81.25 Amps) Fuse: 125 Amps Breaker: 175 Amps
VFD
The VFD manufacturer recommends a minimum breaker size of 100 Amps for a 75 HP VFD.
Actual Motor Load
Since the actual motor load is only 50 HP (65 FLA), the NEC calculations apply.
Recommended Course of Action
Based on the information provided, the following is recommended:
Use #4 AWG wire
From the breaker to the VFD and from the VFD to the motor. This exceeds the NEC requirement and the VFD manufacturer's recommendation.
Install a 175 Amp breaker
As per NEC calculations for a 50 HP motor. This will provide adequate protection for the motor and the VFD.
Use a 125 Amp fuse
For the VFD's input power.
Additional Considerations
Conduit Size
Ensure the conduit size is sufficient for the number of conductors being routed. Refer to NEC Table 350.72(B) for conduit fill requirements.
Grounding
Provide proper grounding for the VFD, motor, and associated equipment.
Overload Protection
Consider using an overload relay for the motor to provide additional protection in case of overcurrents.*
Verification: Have the installation inspected by a qualified electrician to ensure compliance with codes and safety standards. Flag for review