Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Arc Fault protected dishwasher circuit?

User: dhalleron, Location: Louisville, KY

Asked on: Wednesday, February 23, 2011 at 10:32 am EST
Answered on: Tuesday, May 14, 2024 at 1:56 am EDT

Question: I need to add a receptacle in a basement near a wet bar. The walls and ceiling are finished drywall so I cannot get a new circuit to this area without cutting drywall or running surface mount. I am able to fish a wire from an existing receptacle located above the counter on the bar. This is on a 3-wire circuit with a shared neutral to a dishwasher under the bar.My inspector is requiring any new wiring in this area have arc fault protection. My supply house told me Square D does not yet make a QO (not Homeline) series 2-pole 20 amp arc fault breaker.I don?t think a single pole arc fault breaker will work properly on one circuit of this 3-wire circuit with a shared neutral.The inspector told me he would allow me to convert the 3-wire circuit to a 2-wire and put the dishwasher and receptacles on the same circuit. There will only be a couple convenience outlets on the same circuit with the dishwasher. Then I could use a single pole arc fault breaker.Should I expect any problems with a dishwasher on an arc fault breaker? Any other ideas?Thanks.

## Options to Comply with Arc Fault Protection### 2-Pole Arc Fault Breaker As you've mentioned, Square D does not currently offer a QO series 2-pole 20 amp arc fault breaker. Therefore, this option is not available.### Single-Pole Arc Fault Breaker on 2-Wire Circuit Converting the circuit to 2-wire is an acceptable solution per the inspector's request. This will require removing the neutral wire from the circuit and connecting the dishwasher and receptacles to the same hot wire. Dishwasher Compatibility

Dishwashers are not typically affected by arc fault breakers. However, it's always best to check the manufacturer's specifications to confirm.### Other Ideas

Surface Mount Arc Fault Breaker

Consider installing a surface mount arc fault breaker in a small junction box on the drywall. This will provide arc fault protection without the need to cut drywall.


Use a Ground Fault Circuit Interrupter (GFCI)

A GFCI outlet can be installed on the counter near the wet bar. This will provide protection against ground faults but will not meet the inspector's requirement for arc fault protection.## Considerations

Circuit Load

Ensure that the circuit load is within the capacity of the single-pole arc fault breaker (typically 20 amps).


Neutral Return Path:
When converting to a 2-wire circuit, ensure that there is a proper neutral return path for the dishwasher and other devices connected to the circuit. Flag for review

Previous Question Next Question