Topic: Fire Pump Overhead

User: shaw0486, Location: baltimore

Asked on: Wednesday, February 23, 2011 at 11:03 am EST
Answered on: Tuesday, May 14, 2024 at 1:56 am EDT

Question: Hey guys,I have this project that is calling for the service to be over head it is also calling for the fire pump conductors to be fed from over head therefore having a service head. Is this permitted for the fire pump by the NEC?

Yes, it is permitted by the NEC for the fire pump conductors to be fed from overhead and have a service head.According to Section 430.31(B) of the NEC, "Fire pumps shall be connected to an independent feeder. The feeder shall be supplied by the service equipment or another approved source."Section 430.32(A) states, "The fire pump feeder conductors shall be installed in a manner that provides mechanical protection as specified in 230.43 and 230.
50."Overhead conductors are considered to be mechanically protected if they are installed in accordance with Section 396 of the NEC. Section 396.10(C) permits service drops to be installed in accordance with Section 230.
24. Section 230.24(B)(1) requires that service drops be installed not less than 10 feet above any building or other structure, except over roofs.Therefore, as long as the fire pump conductors are installed in accordance with the requirements of Section 396 of the NEC, they are permitted to be fed from overhead and have a service head. Flag for review