User: wonda, Location: Barbados
Asked on: Wednesday, February 23, 2011 at 12:31 pm EST
Answered on: Tuesday, May 14, 2024 at 1:57 am EDT
Question: From my interpretation of article 392.9(A)(1) and 392.11 it suggest that I can install 8No. 4 1/2 core x 500 kcmil (each of 2.5" OD) in a single layer on a 24" ladder tray without a 1 OD spacing between them (i.e. the cables are touching).Assuming the neutral is not a current carrying conductor the ampacity of each cable is give in table 310.16 as 380A (75 degree termination and amb. temp of 30 degree C). The total ampacity of the cables would be 3040A.Is my interpretation correct? Or do I have to space them one diameter apart to use the table 310.16?
According to article 392.11 for tray installations containing only communication cables, power cables, or a combination thereof, the spacing requirement for cables of different sizes is 1 cable diameter. Therefore, you would have to space the cables one diameter apart in order to use the ampacity values in table 310.
16.
Conclusion: Your interpretation is incorrect. You must space the cables one diameter apart to use the table 310.16 ampacity values. Flag for review