Topic: Emergency or Optional system

User: Paul Corbett-Furgal, Location: Logan, Utah

Asked on: Wednesday, February 23, 2011 at 1:26 pm EST
Answered on: Tuesday, May 14, 2024 at 1:57 am EDT

Question: Wondering what you all think. If a required fire alarm system is connected to a Optional Stanby Generator does it automatically change the Stanby generator into a Emergency Standby generator. The fire alarm system meets all code requirements of backup power with its own internal backup batteries and charging system.

NFPA 110 Standard for Emergency and Standby Power Systems

NFPA 110 defines an Emergency Standby Power System (ESP) as a system that "provides power to essential electrical systems for emergency use only." Essential electrical systems include life safety systems such as fire alarms and emergency lighting.NFPA 110 defines a Standby Power System (SPS) as a system that "provides power to designated loads in the event of a primary power failure." SPSs are typically used for non-essential systems, such as HVAC or refrigeration.

Code Requirements

According to NFPA 110, fire alarm systems must be powered by an ESP or an SPS that has been designated as an ESP (known as an Emergency Standby Power System, or ESPS).

Optional Standby Generator

An optional standby generator is typically an SPS that is not designated as an ESPS. It is intended to provide backup power for non-essential systems.

Connection to Fire Alarm System

Connecting a fire alarm system to an optional standby generator does not automatically change the generator's status to an ESPS.

Requirements for ESPS

To be designated as an ESPS, the generator must: Be of sufficient size to power the fire alarm system and other essential electrical systems during an emergency Start automatically within 10 seconds of a power failure Have a separate fuel supply capable of operating for at least 24 hours Be tested monthlyConclusion

Based on the information provided, the optional standby generator in question is not automatically an ESPS simply because it is connected to a fire alarm system. To be designated as an ESPS, it must meet the additional requirements outlined in NFPA 110. Flag for review