Question: I got into a discussion with several of the electricians on my present job, including the foreman. They all said that the code does not allow the use of black, red, and blue on a 480v circuit.I disagreed with them. The code in sections 200.6, and 200.7 specify the color for the grounded circuit conductor, section 250.119 covers the equipment grounding conductor, and section 310.12 covers the grounded circuit conductor, the equipment grounding conductor, and the ungrounded conductors. I can find nothing to back up what they are saying.I know that the code specifys that the stinger circuit must be on the center phase, and marked in orange color....but that is the only specific note for an ungrounded conductor.Also, they say you can not re-identify smaller than #6awg....again they must be confusing their codes sections, taking bits and pieces from 200.6, 200.7, and 250.119.But I may be wrong. So what is it????
You are correct. The National Electrical Code (NEC) does not prohibit the use of black, red, and blue conductors on a 480V circuit.
NEC Sections 200.6, 200.7, 250.119, and 310.12 200.6
Specifies the color code for grounded circuit conductors: white or natural gray.
200.7
Specifies the color code for ungrounded circuit conductors: colors other than white, gray, or green.
250.119
Specifies the color code for equipment grounding conductors: bare, green, or green with yellow stripes.
310.12
Specifies the color code for grounded circuit conductors, equipment grounding conductors, and ungrounded conductors. It allows for any color other than white, gray, or green for ungrounded conductors.
NEC Section 310.15 Specifies the requirements for marking ungrounded conductors on systems over 1000V, but does not apply to 480V circuits.
NEC Section 110.15 This section addresses reidentification of conductors but does not specify a minimum size. It allows for reidentification of conductors if the new identification is consistent with the NEC.
Conclusion
Based on the NEC, there is no prohibition against using black, red, and blue conductors on a 480V circuit, and reidentification of conductors smaller than #6AWG is permitted if done correctly. Flag for review