Question: We just installed a 20kw generator with a service rated xfer switch and load shedding capability on a home.Checked the hz. 59.5-60, but the voltage L-L was 250-251, L1-N 124.5 and L2-N was roughly the same.This was with no load, but does this not seem a little too high? I would like to tweak it down to around 240...but there was no mention of voltage output adjustment in the manual. Do I just idle it down?Another question:The generator is only a 20kw/83a but comes with a 100amp breaker. Using the 75deg. column I used #4, but after reading 110.14(c), that was brought up in a previous thread, I'm wondering if I should have used #3.Thoughts?
Voltage Regulation Yes, 250-251V L-L seems slightly high for a generator rated at 120/240V. Ideally, you want the voltage to be within ±5% of the nominal value, which would be 228-252V for a 240V system. While the generator's manual may not explicitly mention voltage output adjustment, there should be a way to adjust the governor or voltage regulator to fine-tune the output. Consult with the manufacturer or a qualified electrician to determine the proper procedure. Idling the generator down may slightly lower the voltage, but it's not a recommended way to adjust it.
Breaker Sizing According to NEC 110.14(c), the overcurrent protection device for a generator must be rated for no more than 125% of the generator's rated current. In this case, the generator has a rated current of 83A, so a 100A breaker is within the allowable range. #4 wire is rated for 90A at 75°C, which is also within the allowable range. However, if you prefer to use #3 wire, which is rated for 100A at 75°C, it would provide a slightly higher level of protection.
Recommendations: Contact the generator manufacturer or a qualified electrician to adjust the voltage output to within the recommended range. Use #4 wire for the feeder circuit, which is sufficient for the 83A generator. If desired, you could upgrade to #3 wire for added protection. Flag for review