User: marsac, Location: Utah
Asked on: Thursday, February 24, 2011 at 8:28 am EST
Answered on: Tuesday, May 14, 2024 at 1:59 am EDT
Question: Your analysis/opinion on NEC 705.40 (&705.42).You can use a single phase utility interactive inverter in a three phase system if its listing allows.My understanding is part of UL Std. 1741 is the capability to ?Upon loss of primary source, an electric power production source" (the PV inverter) "shall be automatically disconnected??.? or by exception ?cease exporting power?.Our jurisdictions position is that both of the above code references requires a single phase PV source when attached to a 3-phase system to cease exporting power when the primary source loses one or all phases. This would include the phase that the single phase PV inverter is not connected to.We would appreciate your analysis and opinion
Analysis and Opinion
NEC 705.40 requires that single-phase utility-interactive inverters installed in three-phase systems be listed to meet the requirements of UL 1741. This standard includes a requirement for automatic disconnection or cessation of power export upon loss of the primary power source.NEC 705.42 further specifies that single-phase inverters connected to three-phase systems must not export power when any phase of the primary power source is lost.
Interpretation
The intent of NEC 705.40 and 705.42 is to prevent islanding, which is a condition where a PV system continues to generate and export power after the utility grid has lost power. Islanding can pose a safety hazard to utility workers and can damage the grid.In the context of a single-phase PV inverter connected to a three-phase system, the requirements of NEC 705.40 and 705.42 mandate that the inverter must automatically disconnect or cease exporting power upon the loss of any phase of the primary power source. This includes the phase that the inverter is not connected to.
Jurisdiction's Position
The jurisdiction's position is consistent with the intent of NEC 705.40 and 705.
42. By requiring single-phase PV inverters connected to three-phase systems to cease exporting power upon the loss of any phase of the primary power source, the jurisdiction is mitigating the risk of islanding and enhancing safety.
Conclusion
NEC 705.40 and 705.42 require that single-phase utility-interactive inverters installed in three-phase systems must automatically disconnect or cease exporting power upon loss of the primary power source, including the phase that the inverter is not connected to. The jurisdiction's position aligns with this requirement and promotes electrical safety. Flag for review