User: wmeek, Location: Texas
Asked on: Thursday, February 24, 2011 at 10:33 am EST
Answered on: Tuesday, May 14, 2024 at 1:59 am EDT
Question: If you size a motor branch circuit ocp per code. Does the equipment grounding conductor have to be size to the overcurrent device in this situation or just to the Full load current . What I have is:20hp motor at 54A x 250% = 135A up it to 150AConductor 54A x 125% = 67.5A or a #4 Thhn conductor for phase conductorsWhat size would the grounding conductor have to be per code.
According to the National Electrical Code (NEC) Article 250.122, if the branch-circuit overcurrent device is sized to protect the motor branch circuit according to Table 430.152, then the equipment grounding conductor shall be sized to the full-load current of the motor.In this case, the branch-circuit overcurrent device is sized at 150A, which is per Table 430.
152. Therefore, the equipment grounding conductor must be sized to the full-load current of the motor, which is 54A.According to Table 8 of Chapter 9 of the NEC, a #10 THHN conductor is suitable for a current of 60A. Therefore, a #10 THHN conductor would be sufficient for the equipment grounding conductor. Flag for review