Topic: NEC 210.52 (C) (3) Peninsular Countertop Spaces

User: tgolden, Location: NE Arkansas

Asked on: Thursday, February 24, 2011 at 1:35 pm EST
Answered on: Tuesday, May 14, 2024 at 1:59 am EDT

Question: I am an Electrical Safety Inspector with the City of Elyria, Ohio. The State of Ohio is still operating on the 2008 National Electric Code.Recently, I performed a final electrical inspection on a new dwelling within our City. Within the kitchen area an extension of the counter was installed. (Peninsular) During that inspection, I discovered that the peninsular did not have any receptacle(s) installed pursuant to article 210.52 (C) (3). The peninsular meets all the requirements as listed in the article. It also has an overhang at the end of the peninsular and the backside of more than 12 inches. The front side overhangs about 2 inches.After speaking with the electrician, he states that because there is no place on the peninsular or either on the side of the cabinet attached to the peninsular, he is not required to install a receptacle. He quotes the Exception as the reason why he is not required to install the peninsular receptacle. I stated that he is correct as outlined within the exception, he could not mount a receptacle due to the requirements within the exception, but he is still required to have at least one receptacle pursuant to article 210.52 (C) (3). He disagreed with me and stated that the exception allows him to disregard the receptacle if it can not be mounted on the side(s) of the cabinet under the peninsular.Your comments would be helpful. Please reply to this post or PM me. Thank you.

The electrician's interpretation of the Exception to Article 210.52(C)(3) is incorrect.

Article 210.52(C)(3)

"Peninsular Counter Tops. In kitchens and dining rooms, a receptacle outlet shall be installed within 2 feet of the end of a peninsular counter top that extends at least 36 inches from a wall or cabinet. Receptacles shall be mounted on the side or the end of the peninsular counter top."

Exception

"Receptacles are not required on peninsular counter tops where the countertop does not extend beyond the cabinets or walls."The Exception applies only to situations where the peninsular countertop does not extend beyond the cabinets or walls. In this case, the peninsular countertop does extend beyond the cabinets or walls, specifically with an overhang of more than 12 inches on the backside.

Therefore, a receptacle outlet must be installed within 2 feet of the end of the peninsular counter top, even though it may not be possible to mount it on the side(s) of the cabinet.
Justification:

The purpose of Article 210.52(C)(3) is to provide accessible power outlets for appliances and equipment that may be used on peninsular counter tops. The Exception is intended to only exempt peninsular counter tops that are small and do not provide a significant work surface.In the case you described, the peninsular counter top clearly meets all the requirements of Article 210.52(C)(3), including the extension beyond the cabinets or walls and the overhang. Therefore, it requires a receptacle outlet to be installed within 2 feet of its end. Flag for review