User: sparky519, Location: Chapel Hill, NC
Asked on: Thursday, February 24, 2011 at 1:53 pm EST
Answered on: Tuesday, May 14, 2024 at 1:59 am EDT
Question: I understand derating based on bundling and temperature, but how does conduit size come into play. NEC states 16 #12AWG in 3/4 emt based on 40% fill. Bundling adjustments decrease the ampacity of #12 THHN to 15A based on 10 - 20 conductors in a raceway and 21A based on 7 - 9 conductors in a raceway. Does this mean that if I run a 1 1/2" emt that I can only pull 7 - 9 #12 current carrying conductors through it! I hope someone can clear this up since its been a pretty hot topic for arguments on the job.
The National Electrical Code (NEC) does not specifically state that the number of current-carrying conductors that can be installed in a conduit is limited by the conduit size. However, the NEC does require that the conductors be installed in accordance with the manufacturer's instructions.The manufacturer's instructions for THHN conductors typically specify that the conductors can be installed in a conduit with a fill factor of 40%. This means that the cross-sectional area of the conductors cannot exceed 40% of the cross-sectional area of the conduit.The cross-sectional area of a 16 #12 AWG THHN conductor is 0.022 square inches. The cross-sectional area of a 3/4 inch EMT conduit is 0.44 square inches. Therefore, the maximum number of 16 #12 AWG THHN conductors that can be installed in a 3/4 inch EMT conduit is 0.44 square inches / 0.022 square inches / 0.4 = 9.However, the NEC also requires that the conductors be derated for bundling. The derating factor for 10-20 conductors in a raceway is 0.
8. This means that the ampacity of each conductor must be multiplied by 0.8.The ampacity of a 12 AWG THHN conductor is 20 amps. Therefore, the ampacity of a 12 AWG THHN conductor in a raceway with 10-20 conductors is 20 amps x 0.8 = 16 amps.Therefore, the maximum number of 12 AWG THHN conductors that can be installed in a 3/4 inch EMT conduit is 9 x 0.8 = 7.
2.
Conclusion
Based on the NEC and the manufacturer's instructions for THHN conductors, the maximum number of 12 AWG THHN current-carrying conductors that can be installed in a 1 1/2 inch EMT conduit is 7. Flag for review