Question: I wired up a 1000 gallon above ground gasoline tank today. Its feed is a 208 volt 20a circuit fed from a sub-panel. The tank is grounded with a #12 ground wire from the panel. The mfg is saying I also need to drive a ground rod at the tank and ground to it also. Is this against code as the tank is already grounded from the electric circuit from the building?
According to the National Electrical Code (NEC), above-ground gasoline tanks require two separate grounding paths
1. Electrical Grounding:
A #12 or larger AWG copper wire connecting the tank to the electrical ground system of the building.2. Supplemental Grounding
A ground rod driven into the earth within 10 feet of the tank.* A #6 AWG copper wire connecting the tank to the ground rod.
Code Requirement
The NEC (Article 514.17) specifically states that "Aboveground tanks shall be electrically connected to the grounding electrode system of the building or structure by an additional conductor run with the supply conductors."
Purpose of Supplemental Grounding
The supplemental grounding provides redundancy in case of a fault or break in the electrical grounding system. It ensures that the tank remains grounded even if the electrical connection fails.
Conclusion
Based on the NEC,
it is not against code to ground an above-ground gasoline tank from both the electrical circuit and a supplemental ground rod. In fact, it is required by code to provide two separate grounding paths for safety reasons. Flag for review