Topic: Is exterior lighting without a ground-wire permissible?

User: stuartdmc, Location: Newport Beach, Irvine, CA

Asked on: Thursday, February 24, 2011 at 3:54 pm EST
Answered on: Tuesday, May 14, 2024 at 2:00 am EDT

Question: I my town Laguna beach, CA, we have a lot of exterior Christmas tree and twinkle lighting that only has two wires, one hot and one neutral, the city inspector is making all retail and restaurants remove all light fixtures that don't have a ground. I need your help, I am looking for an exception in the code that I can present in our behave.Thank you.

Exception to Grounding Requirement for Exterior Christmas Tree and Twinkle LightingNational Electrical Code (NEC) Section 400.7(A)Exception No. 2

Insulated wire and cable shall not be required to be grounded where installed in the following:>

Luminaires
(fixtures) which are not required to be grounded by Section 250.42Section 250.42Exception

Fixtures

mounted on
or attached to surfaces that are neither conductive nor likely to become conductive.

Interpretation

The exception in Section 400.7(A)(2) allows for the use of ungrounded lighting fixtures in certain situations. Exterior Christmas tree and twinkle lighting typically meet the criteria of this exception because they are:
Luminaires (fixtures) Not required to be grounded by Section 250.42 Mounted on or attached to non-conductive surfaces such as wood, stucco, or brick

Additional Considerations

The lights should be listed for outdoor use and meet the requirements of Underwriters Laboratories (UL). The lights should be installed in accordance with the manufacturer's instructions.* The lights should be checked regularly for any damage or defects.

Recommendation:


Present the above exception and interpretation to the city inspector. Explain that the exterior Christmas tree and twinkle lighting in Laguna Beach meets the requirements of the exception and does not require grounding. Request an exemption from the requirement to remove these light fixtures. Flag for review