Topic: water heater disconnect in clothes closet

User: New EE, Location: California

Asked on: Thursday, February 24, 2011 at 4:12 pm EST
Answered on: Tuesday, May 14, 2024 at 2:00 am EDT

Question: Is there a code requirement against having a water heater disconnect in a residential clothes closet? The owner is putting a water heater in the bedroom closet so I was wondering if there were any electrical code violations by putting a disconnect in there. Thanks.

National Electrical Code (NEC)Article 422.31(A)"Disconnecting means for appliances rated at more than 50 amperes or 120 volts, single-phase, intended to be cord-and-plug-connected shall be located within sight from the appliance terminals."Article 422.31(B)"Exception: For cord-and-plug-connected appliances, the disconnecting means shall be permitted to be located remote from the appliance where all of the following conditions are met

(1) The appliance manufacturer's instructions require a remote location for the disconnecting means.
(2) The cord-and-plug-connected appliance is located within 15 meters (50 feet) of the disconnecting means. (3) The disconnecting means is not located in a bathroom or clothes closet."

Conclusion

Yes, there is a code requirement against having a water heater disconnect in a residential clothes closet.According to NEC Article 422.31(B) Exception 3, the disconnecting means for a cord-and-plug-connected appliance (such as a water heater) cannot be located in a clothes closet. Flag for review