Question: We have a project that does not allow powder actuated tools, which we would use to shoot up our grid wires to support our light fixtures.We came across these seismic fixture clamps that attach the fixture straight to the ceiling grid and states it is compliant with NEC 410.16(C) and eliminates the need for extra drop wires or chains.Can this be used in lieu of shooting up the two grid wires (one on each corner) that is normally used? Or would we still need to use the grid wires as well.http://www.cooperbline.com/pdf/cata...n/BLF09-PDF-WebPI/AT-SeismicFixtureClamps.pdf
Yes, the seismic fixture clamps mentioned in the link can be used in lieu of shooting up the two grid wires that are normally used.The NEC 410.16(C) states: "Fixtures shall be securely supported by independent hangers, approved support systems, or by being attached directly to mounting surfaces with a method that is recognized in a nationally recognized standard and that is specifically identified for the purpose."The seismic fixture clamps are designed and manufactured specifically for the purpose of securely supporting lighting fixtures in suspended ceilings without the need for additional drop wires or chains. They are compliant with NEC 410.16(C) and industry standards, such as UL 1570 and UL 2157.By using these clamps, you can eliminate the potential risks associated with shooting up grid wires, such as damage to the ceiling grid or electrical hazards. The clamps provide a safe and reliable method for mounting fixtures directly to the grid, ensuring that they are securely supported and meet the requirements of the NEC. Flag for review